Remote re-configure a Cyclone IV in Application-mode?
- 7 years ago
Hi JHono,
In your application image design, did you set any write_param on the boot address that point to 0x100000? Please remove any write_param operation in the application image design. If you refer to Table 17: Cyclone IV Devices Remote Update Operation from the Remote Update user guide shows that you can only perform read_param operation in application image:
https://www.intel.com/content/dam/www/programmable/us/en/pdfs/literature/ug/ug_altremote.pdf
Also, please uncheck the POR_ERROR function in the application image design. This POF_ERROR function is only needed in the factory image to detect any invalid application image before reconfiguration process start.
Regards,
Nooraini
Brilliant, that fixed it! Unchecking POF_ERROR makes it boot from 0x000000 and removes some of the functionality of the RSU in the App-image. This means you can't use the same image for Factory & App , if you want POF_ERROR-checking in the Factory image.
Not a problem for me.
Thanks Nooraini.